How do I recognize impending icing over Heishamon (L model) #572
-
Hello everyone, I operate two Panasonic L-model air-to-water heat pumps in cascade mode without a cascade manager. It is controlled by two Heishamon in combination with my home automation system. I would like to find out how I can recognize that the first heat pump is about to freeze up so that I can switch it off and switch on the second heat pump at the same time. I am hoping for no thawing during the wet and cold period. I am looking for specific tips or experience on how to better assess icing. Does anyone have similar experiences or helpful tips? Many thanks |
Beta Was this translation helpful? Give feedback.
Replies: 4 comments 9 replies
-
In service manual for each type there is a "deice chart" - showing at with Outdoor temperature what Outdoor pipe temperature should be. For your can be a little bit different temps. |
Beta Was this translation helpful? Give feedback.
-
This is probably never going to work, de-icing needs some reverse heating of your condensor, not going to happen by itself by the outside temperature, maybe when its 10 degrees above zero but not at the typical outside temperatures where the condensors builds up ice. |
Beta Was this translation helpful? Give feedback.
-
Correct, it does not work. So the graphic fits, but the idea behind it doesn't work. What I have done now: If one heat pump would actually be enough, but the environmental conditions cause frequent defrosting, then the second heat pump will start up anyway and both will run at the minimum setting. According to my tests, this increases the defrosting time considerably (by a factor of more than 2). |
Beta Was this translation helpful? Give feedback.
-
Very curious about your further findings! |
Beta Was this translation helpful? Give feedback.
In service manual for each type there is a "deice chart" - showing at with Outdoor temperature what Outdoor pipe temperature should be.
This is example for M model:
For your can be a little bit different temps.
So you have to implement such graph in your automation , and stop HP 2 minutes after Outdoor pipe temperature drups to this particular value ( depends on Outdoor temperature).
EDIT: You have to implement also this 35minutes.... When you start such freezed HP , it will also run 35min with COP=1 or even below , becouse it will not do the deicing before that....