Replies: 2 comments
-
how pump work differs from Comfort via Efficiency ? |
Beta Was this translation helpful? Give feedback.
-
In comfort mode, the pump starts at a high frequency so that the target temperature is reached as quickly as possible. The problem in efficiency mode is that the target temperature is not reached within the 35min (minimum defrost cycle) before the next defrosting process starts and the temperature in the house slowly decreases. This phenomenon is always the case when the outside temperature is below 2°C and the relative humidity is above 90%. |
Beta Was this translation helpful? Give feedback.
-
Hi Folks
Is it possible to switch the heating control between comfort and efficiency via Heishamom?
In the ProtocolByteDecrypt.md I found the following information...
5th & 6th bit = b01 - Comfort , b10 - Efficiency
I want to switch to Comfort when the outside temperature is low (< 2°C) and the humidity is high, otherwise I will lose heat in the house (due to excessive defrosting).
When the outside temperature is above 5°C, I want to switch back to Efficiency to reduce the cycling.
thanks in advance