Replies: 23 comments 90 replies
-
Der Esp fragt alle 15s ab. |
Beta Was this translation helpful? Give feedback.
-
Oh das war wirklich dann die erste Version.Web Oberfläche hab ich sonst eigentlich immer an gehabt. |
Beta Was this translation helpful? Give feedback.
-
Interesting to read this. Glad I'm not the only one... I had the E81 error a few months ago. On 2024-04-22 +/- 22:30 (last monday evening) my heatpump failed. It has a E100 error with a red screen. This error is not described in the manuals. The error can't be cleared by turning the unit on / off or by clearing through the display. I also noticed:
I'm still able to run a DHW program using the 9kW backup heater. It's a tedious ritual because the unit errors and puts itself into standby. A bit of background on my unit. I bought my it via a German web-shop in 2016 and installed it with a local plumber, electrician and air-conditioner specialist. Note that this model was never sold in the Netherlands. The identical machine was sold in Belgium under the Daikin brand, which must be the reason that Dutch translated manuals exist. The HPSU compact has its quirks with:
Up until this week the unit has been running fine. The only issue I had was a leakage in the DHW circuit, the rubber seals disintegrated. I reached out to Daikin Germany who forwarded me to Daikin Netherlands. The response from Daikin Netherlands was simple: won't support. I've also reached out to a German Rotex (Daikin) employee who has answered some questions I had about the rotex-control app and website and the behavior of the DHW program with high outdoor temperatures. He suggested to check if the flow sensor (FLS) is clean / defective. Similar to this video of a unit one generation older. I de-pressured the system on Tuesday evening but wasn't able to get the sensor out. As all of these parts are plastic and have been in use for 8 years, I'm a bit hesitant to apply too much force to it. If it breaks than I have an even bigger problem --> won't be able to run the DHW program. I find it hard to believe that this could be caused by a contaminated / malfunctioning flow sensor. I think the mainboard has failed. Next steps for me:
I think the E81 and E100 errors are probably caused by sending a lot of requests over the canbus. So if you want your heatpump to last a bit longer.... |
Beta Was this translation helpful? Give feedback.
-
hab jetzt mal eine neue yaml hoch geladen wie einige Daten nur noch alle 120s abgefragt werden. |
Beta Was this translation helpful? Give feedback.
-
Ich hatte sowohl bei der Nutzung des FHEM Moduls, als auch mit diesem Modul hier auch hin und wieder den Fehler 81. |
Beta Was this translation helpful? Give feedback.
-
Long story short: my heatpump is working again. After extensive troubleshooting I was given instructions on how to perform a factory reset of the mainboard. I'd like to investigate if this software can listen to messages on the canbus instead of constantly performing queries on the canbus. On my raspbery pi I ran candump for > 1 hour. My heatslope is at 0.5 (0x32). These are the patterns that match:
Would it be possible to change this:
So it listens for messages:
These are the other messages, probably from devices performing the query:
|
Beta Was this translation helpful? Give feedback.
-
Ich habe mich da letzte Woche mit beschäftigt und schon eine neue YAML geschrieben. |
Beta Was this translation helpful? Give feedback.
-
Aber dafür ist es ja auch da um es immer wieder besser zu machen.👍 |
Beta Was this translation helpful? Give feedback.
-
Also ohne Abfrage kommen bei mir keine Werte an. |
Beta Was this translation helpful? Give feedback.
-
Just connected the esphome device to the heatpump. In the yaml I've disabled the entire section time section (CAN Nachrichten abfragen). So the only data it should get is what it finds while listening to the canbus. The listening filter for "Heizkurve" now looks like this:
The heizcurve just changed from 0.48 (the value I was running before the crash) to 0.5. |
Beta Was this translation helpful? Give feedback.
-
For the outside temperature:
|
Beta Was this translation helpful? Give feedback.
-
Hello I am also facing the same Error 81 issue. It happened quite a lot of times, I thought it was due to bad cables/connections but I see I'm not the only one. I have tried to install the latest version of the software and removing all the CAN polling. However, now I basically can see only the operating mode (Summer, Heating, etc.). All other important parameters are not sent by the HPSU without the polling. I was liking a lot this software and I would really like to continue using it, it has been super helpful! However, I am afraid that I might damage the unit if I keep having these errors. Is it possible to damage the HPSU with the continuous CAN polling or am I just afraid of nothing? Thanks for the help :) |
Beta Was this translation helpful? Give feedback.
-
@Trunks |
Beta Was this translation helpful? Give feedback.
-
Bitte einmal die neue .bin testen ob der Fehler 81 noch auftritt bzw weniger oft vorkommt. |
Beta Was this translation helpful? Give feedback.
-
Ich finde im File Editor die Datei /homeassistant/secrets.yaml muss ich es in die Datei eintragen? |
Beta Was this translation helpful? Give feedback.
-
Also zu Fehler E 81 kann ich folgendes berichten. Meine HPSU Compact habe ich seit 10 Jahren mit dem Rocon G1 Gateway in Betrieb. Alles ohne Probleme. Ich habe jetzt seit ca. 2 Monaten die Lösung von Trunks 1982 in Nutzung. Wirklich großartiges Projekt und die Integration in HA läuft super. RaikertHA |
Beta Was this translation helpful? Give feedback.
-
Hast du mal nen eprom reset gemacht? |
Beta Was this translation helpful? Give feedback.
-
Nein ein Reset des EPROM habe ich noch nicht gemacht. Aber ich habe heute die aktuelle Version 1.5.1 drauf geladen (vorher 1.3.6) und das OTA Update hat auch funktioniert. Ich teste jetzt die Tage mal die Konfiguration und melde mich nochmal. Danke erstmal für die schnelle Antwort.Viele Grüße RaikertHAAm 25.08.2024 15:34 schrieb Trunks1982 ***@***.***>:
Hast du mal nen eprom reset gemacht?
—Reply to this email directly, view it on GitHub, or unsubscribe.You are receiving this because you commented.Message ID: ***@***.***>
|
Beta Was this translation helpful? Give feedback.
-
Hatte bislang 1.3.6. seit heute die aktuelle 1.5.1.Ich gebe Bescheid die Tage.Danke für die schnelle Antwort.Viele Grüße RaikertHAAm 25.08.2024 15:12 schrieb fajen1 ***@***.***>:
Zwischenfrage, hast du die aktuelle Version drauf?
—Reply to this email directly, view it on GitHub, or unsubscribe.You are receiving this because you commented.Message ID: ***@***.***>
|
Beta Was this translation helpful? Give feedback.
-
Hi, leider hat´s meine Hauptplatine jetzt wohl voll erwischt, Entweder Fehler 8100 Kessel und die andere weiß ich leider im Moment nicht mehr genau. Anlage ist jetzt ziemlich genau sieben Jahre alt. Es begann, dass auf dem Display keine Werte mehr angezeigt wurden. Auf der ESP-Site stand u.A. Temperatur an der Außeneinheit -40°C. Die Außeneinheit lief für ein paar Sekunden an und ging wieder aus. |
Beta Was this translation helpful? Give feedback.
-
Nach 2 Wochen Betrieb mit Version 1.5.1 habe ich jetzt wieder den E 81 auf dem Display :( |
Beta Was this translation helpful? Give feedback.
-
Nach dem ich heute wieder einen E81auf dem Display hatte (habe die Version 1.5.1 in Nutzung und alle Delays auf 500 ms hochgesetzt gehabt, um ggf. eine langsame Lese/Schreibperformance der ROTEX auszugleichen)habe ich die Kabel heute alle nochmal erneuert. Ich beobachte jetzt weiter. Eine Frage: Klappt bei euch die 1x WW Aufbereitung? Wenn ich den Knopf drücke, passiert bei mir leider überhaupt nichts. :( |
Beta Was this translation helpful? Give feedback.
-
Hallo,
meine Heizung zeigt mittlerweile fast täglich den Fehler E81 Kessel.
Laut Anleitung von Heizung konnten wohl die Werte nicht ins EEPROM geschrieben werden.
In der Anleitung vom Rotex externen CAN Bedienteil steht, das ein ungültiger Wert übermittelt worden ist.
Ich habe das Kabel zwischen ESP und HPSU gegen ein CAT6 TP Kabel getauscht und den Schirm an der Heizung auf GRD gelegt.
Trotzdem war der Fehler heute morgen wieder da.
Kennt jemand das Problem?
Ich habe schon sämltliche Automatiken deaktiviert.
Noch eine Frage habe, ich:
Pollt der ESP die CAN Register auf der Heizung, oder werden diese (RS232 like) von der Heizung im Intervall gesendet und nur empfangen?
Beta Was this translation helpful? Give feedback.