Error on Canbus for JKBMS #61

Closed Answered by rogergrant99
rogergrant99 asked this question in Q&A
Discussion options

You must be logged in to vote

After looking at CAN data I am thinking that there can only be one BMS per CAN buss. The way I understand it is that the message ID is the only ID provided.... Therefore both BMS send exactly the same ID messages. So I tried to connect one BMS to CAN0 and the other to CAN1 and after a bit of code modification (so the identifier is unique) I got it to work correctly.
Also I discovered that the message ID for CELL_VOLT and CELL_TEMP was different when connected to CAN1 vs CAN0 (but the BATT_STAT is correct...) That one I could not figure out, I don't know if some manipulation is done in the Cerbo before CAN messages are captured... So I added the new (or rewritten) frame id for the CELL_VOL…

Replies: 5 comments 8 replies